AWS D1.1:2025 · 条項 7.13 · Table 7.7

D1.1 Minimum すみ肉溶接サイズ: Table 7.7 Explained

Table 7.7 sets minimum すみ肉溶接の脚長 sizes based on 母材 板厚. For material over 3/4 in, the minimum is 5/16 in. Footnote a changes which thickness controls depending on whether you use a 低水素 process — a distinction most references skip entirely.

What Clause 7.13 Requires

Clause 7.13 of D1.1:2025 states that the minimum すみ肉溶接 size, except for fillet welds used to reinforce groove welds, shall be as shown in Table 7.7. The minimum fillet 溶接サイズ shall apply in all cases, unless the design drawings specify welds of a larger size.

This is a 製作 requirement, not a design requirement. The Engineer sizes the weld based on load. Table 7.7 establishes a floor — the weld can never be smaller than the table value for a given base metal thickness, regardless of what the calculated load would allow.

Table 7.7: Minimum Fillet Weld Sizes

Table 7.7 — D1.1:2025 Minimum Fillet Weld Sizes
Base Metal Thickness (T)Minimum Fillet Weld Size
T ≤ 1/4 in [T ≤ 6 mm]1/8 in [3 mm]
1/4 in < T ≤ 1/2 in [6 < T ≤ 12 mm]3/16 in [5 mm]
1/2 in < T ≤ 3/4 in [12 < T ≤ 20 mm]1/4 in [6 mm]
3/4 in < T [20 mm < T]5/16 in [8 mm]

Three footnotes modify how you read this table. Each one addresses a situation that changes the effective requirement. Most online references reproduce the four rows above and stop there. The footnotes are where the real 基準 knowledge lives.

Footnote a: Which Thickness Is T?

Footnote a is the most consequential note in Table 7.7. It defines what T means, and the answer depends on your 溶接工程:

Non-low-hydrogen processes without 予熱 calculated per Clause 6.8.4: T equals the thickness of the thicker part joined. Single-pass welds shall be used. This means your minimum weld size is driven by the heavier member, and you must deposit the full size in one pass.

Low-hydrogen processes (and 非低水素 with preheat calculated per Clause 6.8.4): T equals the thickness of the thinner part joined. The single-pass requirement does not apply. This means your minimum weld size is driven by the lighter member, and you can build up the size in multiple passes.

Consider a joint between a 1 in column flange and a 3/8 in connection plate. With E7018 (low-hydrogen), T = 3/8 in (thinner part), so the minimum fillet weld is 3/16 in. With E6013 (non-low-hydrogen, no preheat calculated per 6.8.4), T = 1 in (thicker part), so the minimum jumps to 5/16 in — and it must be deposited in a single pass.

If you need to determine whether your process qualifies as low-hydrogen for Table 7.7 purposes, start with your preheat requirements — the 電極分類 drives both the preheat カテゴリー and the footnote a interpretation.

The reason for this distinction is metallurgical. Non-low-hydrogen electrodes produce higher 拡散性水素 in the weld deposit. A thicker base metal acts as a larger heat sink, cooling the weld faster and increasing the risk of hydrogen-induced cracking. Requiring the minimum size to be based on the thicker member ensures adequate 入熱 into the joint. The single-pass restriction prevents the 溶接士 from depositing a thin first pass that cools too rapidly against the heavy member.

A 製作者 溶接 3/8 in gusset plates to W14x90 column flanges (flange thickness approximately 0.710 in) with E7018 uses T = 3/8 in (thinner part). The minimum fillet weld is 3/16 in. If the shop switches to FCAW-S with a non-low-hydrogen wire and does not have preheat calculated per Clause 6.8.4, T becomes 0.710 in (thicker part) and the minimum jumps to 1/4 in, single pass only. Same joint, different process, different requirement.

Footnote b: The Thin-Member Escape Clause

Footnote b states that the weld size need not exceed the thickness of the thinner part joined. This prevents an absurd 結果 when a very thin member is attached to a very thick one.

If you weld a 3/16 in gusset to a 1-1/2 in thick base plate using E7018, Table 7.7 would require a 3/16 in minimum fillet (T = 3/16 in, thinner part). That happens to equal the gusset thickness, which is fine. But if someone welded the same gusset with a non-low-hydrogen process (T = 1-1/2 in, thicker part), the table would call for 5/16 in — larger than the gusset itself. Footnote b caps the requirement at 3/16 in, the gusset thickness.

In practice, footnote b most often applies when thin plates, angles, or channels are connected to heavy wide-flange sections. The Engineer will typically specify a weld size based on load, and that calculated size will usually govern over the Table 7.7 minimum for thin-to-thick joints.

Footnote c: Cyclic Loading Override

Footnote c states that the minimum size for cyclically 読み込み済み structures shall be 3/16 in [5 mm]. This overrides the 1/8 in [3 mm] value in the first row of the table.

For base metal 1/4 in and under in a statically loaded structure, the minimum fillet weld is 1/8 in. For the same thickness in a cyclically loaded structure — a bridge, a crane runway girder, or any connection subject to fatigue — the minimum increases to 3/16 in. The second through fourth rows already require 3/16 in or more, so footnote c only changes the outcome for the thinnest material.

The rationale is fatigue performance. A 1/8 in fillet weld on a cyclically loaded joint has minimal throat area to resist repeated stress reversals. The 3/16 in floor provides a larger 有効のど厚 and a less severe stress concentration at the 溶接止端.

How Table 7.7 Interacts with Design Requirements

Table 7.7 is a minimum, not a design tool. The Engineer calculates the required weld size per Clause 4 based on applied loads. If the calculated size exceeds the Table 7.7 minimum, the calculated size governs. If the calculated size is less than the Table 7.7 minimum, the table value governs.

There is also an upper limit. Clause 4.5.2.9 限界値 the 最大 fillet weld size on the edge of material less than 1/4 in thick to the material thickness. For material 1/4 in or greater, the maximum size along edges shall be 1/16 in less than the material thickness, unless the weld is specifically designated on the drawings to be built out to obtain full 溶接のど厚.

These constraints create a window: your fillet weld must be at least the Table 7.7 minimum and no more than the Clause 4.5.2.9 maximum (when welding along an edge), with the Engineer’s calculated size falling somewhere in between.

D1.1 Table 7.7 vs AISC Table J2.4

AISC 360 Table J2.4 also specifies minimum fillet weld sizes, but it always uses the thickness of the thicker part joined — with no process distinction. D1.1 Table 7.7 footnote a makes the controlling thickness depend on whether you use a low-hydrogen process. When D1.1 is the contract document, Table 7.7 governs. In practice, AISC Table J2.4 is more conservative for low-hydrogen processes because it does not allow you to use the thinner part. If your project references both AISC 360 and D1.1, the more restrictive requirement applies unless the Engineer specifies otherwise.

Common Mistakes

Ignoring footnote a entirely. Many fabricators and even some inspectors read only the four rows and always use the thicker member. With low-hydrogen processes, this overestimates the requirement and wastes 溶加材 and time.

Using multi-pass with non-low-hydrogen electrodes. When footnote a requires single-pass welds, a two-pass fillet deposited with E6013 does not comply, even if the final size meets the table. The 検査員 can reject the weld on procedure alone.

Forgetting footnote c on cyclic structures. A 1/8 in fillet weld on a bridge connection fails the minimum regardless of load calculation. The 3/16 in cyclic floor applies.

Confusing minimum size with design size. Table 7.7 does not replace the Engineer’s weld size calculation. A WPS that calls out 3/16 in because the table minimum is 3/16 in, when the connection actually requires 5/16 in per the design drawings, is undersized.

Once the weld is deposited, the inspector evaluates it against Table 8.1 受入基準. An undersized fillet weld is one of the discontinuities addressed there. For the full list of 外観検査 criteria, see the weld defects overview.

Frequently Asked Questions

It depends on the welding process. Footnote a states that for non-low-hydrogen processes without preheat calculated per Clause 6.8.4, T equals the thickness of the thicker part joined. For low-hydrogen processes and for non-low-hydrogen processes with preheat per Clause 6.8.4, T equals the thickness of the thinner part joined. This means the same joint can require a different minimum weld size depending on whether you use E7018 or E6013.

Only with low-hydrogen electrodes or when preheat is calculated per Clause 6.8.4. Footnote a requires single-pass welds when using non-low-hydrogen processes without preheat calculated per 6.8.4. With low-hydrogen processes, the single-pass requirement does not apply, so you can build up the minimum size in multiple passes.

Yes. Footnote c to Table 7.7 states that the minimum size for cyclically loaded structures shall be 3/16 in (5 mm). This overrides the 1/8 in minimum that would otherwise apply for base metal 1/4 in and under. For thicker material the table values already meet or exceed 3/16 in, so footnote c only changes the first row.

No. Footnote b states that the weld size need not exceed the thickness of the thinner part joined. If you are welding a 3/16 in gusset plate to a 1 in thick column flange, Table 7.7 would require 5/16 in based on the 1 in thickness, but footnote b limits the requirement to 3/16 in because that is the thickness of the thinner part.

For base metal over 3/4 in thick, Table 7.7 requires a minimum fillet weld size of 5/16 in (8 mm). This applies to 1 inch plate when using a low-hydrogen process. If using a non-low-hydrogen process without preheat calculated per Clause 6.8.4, T equals the thicker part, so the 5/16 in minimum still applies. Remember that footnote b allows a smaller weld if the thinner part joined is less than 5/16 in.